Conductor Screen - Triple extrution - Power cable

  • Peter J Stewart-Hay
  • Topic Author
  • Offline
  • Moderator
  • Moderator
More
10 years 4 months ago - 10 years 4 months ago #2789 by Peter J Stewart-Hay
Conductor Screen - Triple extrution - Power cable was created by Peter J Stewart-Hay
We received this message by E-mail and have placed a copy here.


Hello Sir,

I would like to find more information regarding conductor screen for Triple extrusion - 11KV power cable.

Regards
Choe

Regards,
Peter J. Stewart-Hay Principal
Stewart-Hay Associates
www.Stewart-Hay.com
This email address is being protected from spambots. You need JavaScript enabled to view it.
Last edit: 10 years 4 months ago by Peter J Stewart-Hay.

Please Log in to join the conversation.

  • Peter J Stewart-Hay
  • Topic Author
  • Offline
  • Moderator
  • Moderator
More
10 years 3 months ago - 10 years 3 months ago #2790 by Peter J Stewart-Hay
Replied by Peter J Stewart-Hay on topic Conductor Screen - Triple extrution - Power cable
The conductor screen is made from XLPE and is semi-conducting in nature by the addition of carbon.. The compound can be super-smooth by having the carbon produced by burning acetylene as this gives a very small sized particulate.

The conductor screen has three basic functions.

(1) To reduce and smooth electrical stresses at the inside surface of the insulation.

(2) To mechanically protect the insulation from the conductor. This prevents electrical stress concentrations at the conductor surface of the insulation.

(3) Because polyethylene has a larger thermal coefficient of expansion and contraction than the conductors, the plastic will expand away from the conductor. Because the conductor screen is at the same potential as the conductor, there cannot be a flashover. Both screens are obviously very important.

The conductor screen and the insulation screen are simultaneously extruded with the insulation.

Regards,
Peter J. Stewart-Hay Principal
Stewart-Hay Associates
www.Stewart-Hay.com
This email address is being protected from spambots. You need JavaScript enabled to view it.
Last edit: 10 years 3 months ago by Peter J Stewart-Hay.