8 years 3 months ago #2925 by Mr kumar M
hdpe for ehv cable was created by Mr kumar M
Hello,
I want to know that why in ehv cables above 66 kV HDPE is prefered for outer jacketing than PVC .

Regards
Kumar M

Please Log in to join the conversation.

More
8 years 3 months ago - 8 years 3 months ago #2926 by Peter J Stewart-Hay
Replied by Peter J Stewart-Hay on topic hdpe for ehv cable
Hello

PVC is a mixture of a number of chemicals and clay. Sheaths of PVC are generally for inside use but I am aware in Japan of XLPE, EHV cables up to 225 kV.back in the 1970s and they had PVC sheaths.

In contrast, polyethylene is a polymer to which a number of chemicals have been added. (UV resistant chemicals, color pigment, anti-oxidants and so on.) High density polyethylene is also tougher than low or medium density polyethylene. Polyethylene in general well matches the thermal properties of the HV and EHV, XLPE cable cores and is excellent in providing damage and corrosion protection to the heavy cables over the long haul. That is why it is specified .

Thank you.

Regards,
Peter J. Stewart-Hay Principal
Stewart-Hay Associates
www.Stewart-Hay.com
This email address is being protected from spambots. You need JavaScript enabled to view it.
Last edit: 8 years 3 months ago by Peter J Stewart-Hay.

Please Log in to join the conversation.

  • Mr kumar M
  • Topic Author
  • Offline
  • Fresh Boarder
  • Fresh Boarder
More
8 years 3 months ago #2927 by Mr kumar M
Replied by Mr kumar M on topic hdpe for ehv cable
Thanks sir,
But I also want to know why we use a layer of graphite over sheath in ehv cables

Regards
Mandeep

Please Log in to join the conversation.

More
8 years 3 months ago - 8 years 3 months ago #2928 by Peter J Stewart-Hay
Replied by Peter J Stewart-Hay on topic hdpe for ehv cable
Hello again,

In India, a dual sheath is used. The first layer is the standard polyethylene material and the outer layer is semi-conducting, non cross-linked polyethylene. The reason for this is to electrically check at the factory if there are any holes or discontinuities in the first layer.

Perhaps, in your country or area, they are checking the continuity of the sheath at the factory by using a graphite coating.

Regards,
Peter J. Stewart-Hay Principal
Stewart-Hay Associates
www.Stewart-Hay.com
This email address is being protected from spambots. You need JavaScript enabled to view it.
Last edit: 8 years 3 months ago by Peter J Stewart-Hay.