Is there a formula to convert what a 1500mm2 stranded copper cable would be into an equivalent solid diameter? Or something approximately close?
Please Log in to join the conversation.
- Archived Forum Admin
-
Topic Author
- Offline
- Platnium Boarder
-
13 years 3 months ago #216
by Archived Forum Admin
Replied by Archived Forum Admin on topic Re: Need a formula for strand to solid diameters
Hi there Bill,
- Determine the area of one strand after accurately measuring the strand diameter. (They all have the same diameter in this case.)
- Multiply the strand area by the total number of strands to get the area of the conductor you have now.
- Determine the diameter of the solid, round equivalent conductor by working backwards from that combined area.
Go here www.stewart-hay.com/pshwire.htm if you wish to cross check the gauge size of the equivalent solid conductor. (It should be the same gauge size.)
The only difference is that the solid equivalent conductor will have a smaller outside diameter. That is the price that is paid for flexibility.
Other conversions are also on that page.
Regards
Peter J. Stewart-Hay
Principal
Stewart-Hay Associates
www.Stewart-Hay.com
519 641- 3212
- Determine the area of one strand after accurately measuring the strand diameter. (They all have the same diameter in this case.)
- Multiply the strand area by the total number of strands to get the area of the conductor you have now.
- Determine the diameter of the solid, round equivalent conductor by working backwards from that combined area.
Go here www.stewart-hay.com/pshwire.htm if you wish to cross check the gauge size of the equivalent solid conductor. (It should be the same gauge size.)
The only difference is that the solid equivalent conductor will have a smaller outside diameter. That is the price that is paid for flexibility.
Other conversions are also on that page.
Regards
Peter J. Stewart-Hay
Principal
Stewart-Hay Associates
www.Stewart-Hay.com
519 641- 3212
Please Log in to join the conversation.
Moderators: Erik A Macs, Peter J Stewart-Hay
- Resources
- Products/Services
- WAI Forums
- Technical Divisions
- Electrical
- Need a formula for strand to solid diameters
Time to create page: 0.061 seconds